Something to seriously consider is if the gas piping system in your house will provide adequate volume of natural gas to that bitchen new tankless water heater with endless hot water.
Your old tank water heater was probably burning about 35,000 btu. The fancy new Navien tankless heater are gobbling up 199,000 btu. For conversion, 100 cubic feet of gas equals about 103,700 btu. That Navien tankless is consuming almost 200 cubic feet.
If you see 1/2" metal pipe coming out of the wall at your water heater, be nervous. It may have easily served your old tank heater, but for just 10 feet of pipe, 1/2" only provides 131 cubic feet (and the chart only goes down from there), and so would be insufficient for a tankless. I would hope to see 3/4" pipe at your water heater if you're considering a tankless.
It's worth doing a schematic of your gas system from the meter to all of your gas appliances, to make sure you have the piping to deliver the necessary volume. There are several online schematic helpers to do this.
I came here just to post this. To get enough BTU's for a tankless setup, you're looking at needing a 1.5" gas service. If you already have that at the meter, great. If not, upgrading your entire gas system from the street can get VERY expensive.
edit: and MTT, if you're on a city connection, you shouldn't need an upgrade to water service. 100 psi and you're not upping the flow out of the showerhead, that's just fine.